Where is the hydrogen sulfide detection probe mounted?

H₂S is heavier than air. Put the head at low points — trenches, pump pits, sour-water sumps — typically 0.3–0.5 m, not under the roof like methane.

US/EU jobs follow the hazardous-area drawing and OSHA confined-space logic: indoor heads close to the release, outdoor heads where the plume actually travels. High alarm should start extract, not just a beacon.

Calibrate with H₂S cylinder gas. A combustible mix is not a substitute.

Adopt wall-mounted or tube-mounted type; The distance between the transmitter and the release source should not be greater than 2 meters outdoors and 1 meter indoors.